Beauly wrote:Hello Jordy
I take it you mean to increase the pressure as shown on dial on the boiler.
There is a blue knob on the underside of the boiler. On turning this anti clockwise, thus adding more water into the system and increasing the pressure to between 1.5 to 2.00. Is this what you mean?
If you could let me know.
Thank you for your help once again
Regards
Sorry for the delay. Yes, that's the one. Just open it slowly until you hear water starting to run then watch
your pressure dial. Once it reaches 1 to 1.5 close the valve again & that's you done for the season.
I see you have already done this so when your system is up & running and the dial shows 2 or higher
just go to the furthest radiater & bleed a bit of pressure out to bring it just a bit lower. If the boiler
thinks the pressure is too high it will just switch off. Easy peasy.